RCDD-001 Exam - Question 58


You are designing a telecommunications grounding system for a telecommunications room (TR). The TMGB is located 15 m (50 ft) from the telecommunications rack. What is the MINIMUM AWG of the ground conductor required?

Show Answer
Correct Answer: D

For telecommunications grounding systems, the minimum American Wire Gauge (AWG) for a ground conductor over distances up to approximately 30 meters (100 feet) is 6 AWG. Since the distance between the TMGB and the telecommunications rack is 15 meters (50 feet), a 6 AWG ground conductor is required.

Discussion

1 comment
Sign in to comment
CUB90Option: D
Nov 18, 2023

TDMM page 8-22 (788) In most applications, where any bonding conductor does not exceed ~30m (100 ft), a minimum of a 6 AWG bonding conductor is sufficient.