RCDD-001 Exam - Question 65


You are designing a telecommunications grounding system for a telecommunications room (TR). The TMGB is located 15 m (50 ft) from the telecommunications rack. What is the MINIMUM AWG of the ground conductor required?

Show Answer
Correct Answer: D

For telecommunications grounding systems, the minimum American Wire Gauge (AWG) for a ground conductor over distances up to approximately 30 meters (100 feet) is 6 AWG. Since the distance between the TMGB and the telecommunications rack is 15 meters (50 feet), a 6 AWG ground conductor is required.

Discussion

2 comments
Sign in to comment
CUB90
Nov 19, 2023

TDMM page 8-22 (788) In most applications, where any bonding conductor does not exceed ~30m (100 ft), a minimum of a 6 AWG bonding conductor is sufficient.

8e5c2e4Option: D
Jan 5, 2025

TDMM 14 pg 8-20