Exam RCDD-001 All QuestionsBrowse all questions from this exam
Question 32

In the ceiling zone method of distribution, the usable floor area should be divided into zones each measuring:

    Correct Answer: C

    In the ceiling zone method of distribution, the usable floor area is typically divided into zones that measure between 23 square meters (250 square feet) and 84 square meters (904 square feet). This range ensures efficient use of space and allows for manageable zone sizes in terms of access and connectivity.

Discussion
waldo31Option: C

In the ceiling zones method of ceiling distribution, the usable floor area should be divided into zones of ≈23.2 m2 (250 ft2) to ≈92.9 m2 (1000 ft2) each

Davario

Pag 528

RenhoekOption: E

In DD102 they directs us to design with 1000 sq ft zones

waldo31Option: B

correct answer : conduit should be used for each zone ranging from ≈23.2 m2 (250 ft2) to ≈55.7 m2 (600 ft2). This is based on ≈5.6 m2 (60 ft2) to ≈9.3 m2 (100 ft2) work areas and the diameter of the cable no larger than 6.3 mm (0.25 in). For larger zones ranging from ≈55.7 m2 (600 ft2) to ≈84 m2 (904 ft2), an ≈63 mm (2-1/2 trade size) conduit