The MINIMUM recommended lighting requirement in a telecommunications room (TR) at the point of cable terminations is:
The MINIMUM recommended lighting requirement in a telecommunications room (TR) at the point of cable terminations is:
TDMM 14 pg 3-9 - "a minimum of =500 Ix (46 foot-candles) of lighting in the horizontal plane and ~200 Ix (18.6 foot-candles) in the vertical plane, measured =1 m (3.28 ft) above the finished floor in the middle of all aisles between cabinets and racks."